That's exactly the way we see it...these municipalities and local governments are so desperate to generate additional revenue stream in the form of fines that they are becoming zealots on a witch hunt...with no regard as to the economic ramifications of their actions.
John W. Farabee ________________________________ From: Justin Reid <[email protected]> To: [email protected] Sent: Tue, November 15, 2011 8:58:10 AM Subject: Re: NFPA 14 65 to 100 psi Pressure Sounds like an unfair situation. If the comments come back the same, I would ask the owner to attend the next meeting and to elevate it past the reviewer. Obviously their building does not have the infrastructure to even accommodate the reviewers request which is onerous. The reviewer is asking for a major project when all you are doing is repairing an existing component of an existing system. Good luck! Justin Reid On Tue, Nov 15, 2011 at 8:52 AM, 321 <[email protected]> wrote: > Not in a rural area...Major SE Florida Metropolitan City. > > John W. Farabee > > > > > > ________________________________ > From: Andy <[email protected]> > To: [email protected] > Sent: Tue, November 15, 2011 8:37:54 AM > Subject: RE: NFPA 14 65 to 100 psi Pressure > > Are you in a rural area were the he may be concerned about his fire truck > providing adequate pressure to work his new hose nozzles that want a 100 > PSI. > > Thank you, > Andy > > Andy Johnston | Master Craft Plumbing and Fire Protection > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of 321 > Sent: Tuesday, November 15, 2011 8:23 AM > To: [email protected] > Subject: Re: NFPA 14 65 to 100 psi Pressure > > Yes...code required Class II & Sprinkler 30 years ago when building was > built. > Original pump is 500 GPM (locked up...and scrap) limited service 30 > Horsepower. > AHJ first required controller jump to internal auto transformer then came > back > with this 100 psi deal. Customers electric service and emergency gen set > won't > handle the load. > > AHJ is saying he wants pump and standpipe now to comply with current 100 > psi > > requirements...so I said ...ok...in that case he only needs a pump if his > sprinkler demand on the 5th floor requires it. AHJ is now delaying approval > of > change out while he tries to manufacture a counter to our last submittal > ....he > has had it for 15 days now and seems to be stumped. BTW...5th floor calcs > need > the 500 gpm at 65 + city to work as piped. Best all around deal is to R & R > existing pump/controler....owner has 3: identical buildings like this all > built > at the same time ...so we are trying to get the deal right the first time > with > the city. > > John W. Farabee > > > > > > ________________________________ > From: Ron Greenman <[email protected]> > To: [email protected] > Sent: Mon, November 14, 2011 11:01:05 PM > Subject: Re: NFPA 14 65 to 100 psi Pressure > > So why a pump to begin with? Class II pipe? > > On Mon, Nov 14, 2011 at 7:29 PM, 321 <[email protected]> wrote: > > > In a related matter...anyone had an AHJ require upgrade to 100 psi from > 65 > > psi > > when replacing a bad Fire Pump ? I have one I am fighting now in an > > existing > > fully sprinkled building less than 75' in Florida. The AHJ says it must > be > > upgraded in the change out to provide 100 psi. The Florida uniform > > building code > > says that a Fully Sprinkled building under 75' need have only a > manual-wet > > standpipe. > > > > Any thoughts on this? > > > > John W. Farabee > > > > > > > > > > > > ________________________________ > > From: Justin Reid <[email protected]> > > To: [email protected] > > Sent: Mon, November 14, 2011 3:25:25 PM > > Subject: Re: NFPA 14 65 to 100 psi Pressure > > > > Thanks for the quick response! > > > > Justin Reid > > > > On Mon, Nov 14, 2011 at 3:20 PM, Steve Leyton < > [email protected] > > >wrote: > > > > > 1993 > > > > > > > > > Steve Leyton > > > > > > > > > > > > > > > -----Original Message----- > > > From: [email protected] > > > [mailto:[email protected]] On Behalf Of Justin > > > Reid > > > Sent: Monday, November 14, 2011 12:20 PM > > > To: [email protected] > > > Subject: NFPA 14 65 to 100 psi Pressure > > > > > > Does anyone recall off the top of their heads which edition of NFPA 14 > > > the > > > pressure requirements for 2 1/2 inch hose outlets went from 65 psi to > > > 100 > > > psi? > > > > > > Thanks, > > > > > > Justin Reid > > > -------------- next part -------------- > > > An HTML attachment was scrubbed... > > > URL: > > > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach > > > ments/20111114/c779adc5/attachment.html> > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: > > < > > > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20111114/00a23dc3/attachment.html > >l > > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: < > > > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20111114/b345a3d3/attachment.html > >l > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology > Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC > > They are happy men whose natures sort with their vocations. -Francis Bacon, > essayist, philosopher, and statesman (1561-1626) > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20111114/07631e57/attachment.html> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20111115/f1a6dd2f/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < >http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/856e0d57/attachment.html >l > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/b73b3545/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/fc10ba65/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum