Thanks, that's what I thought since the in rack sprinklers are not
calculated with the traditional area-density method.  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Sent: Wednesday, December 14, 2011 6:47 PM
To: [email protected]
Subject: RE: DI pre-action racks

Dwayne,
I don't believe it applies to the in-racks.  There is no mention for
additional sprinklers on in-racks if they are on dry systems to my
knowledge.



Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, December 14, 2011 3:01 PM
To: SprinklerFORUM
Subject: DI pre-action racks

Does the 30% area increase requirement apply to in-rack sprinklers also?
I would think it only applies to the overhead and not to the in-racks
but just wanted to check.

 

Thanks,

Dewayne Martinez

Design Build Fire Protection

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20111214/7871b710/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1873 / Virus Database: 2108/4679 - Release Date:
12/13/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to