This may sound like a Ron Greenman answer, but infinity is greater than 3 ft, so you should be good.
If the ceiling is flat and only supported by the walls, they would be considered "exposed members". As long as the walls are more then 3 ft apart, I would assume you can use the 225 sqft. At 09:23 AM 1/13/2012, you wrote: >According to Table 8.6.2.2.1(a) in the 2010 ED of 13, You can space SSP's >at 225 sq ft if "Combustible unobstructed with exposed members 3 ft or more >on center" > >However, there is no mention of the same scenario minus the exposed members >- am I missing something? This question was asked by a local guy and I >don't guess I have a conclusive answer... > >Thanks, >Greg > >-- >Greg McGahan >Living Water Fire Protection, LLC <http://www.livingwaterfp.com> >1160 McKenzie Road >Cantonment, FL 32533 >850-937-1850 >fax 850-937-1852 >-------------- next part -------------- >An HTML attachment was scrubbed... >URL: ><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120113/d3422608/attachment.html> >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum