This may sound like a Ron Greenman answer, but infinity is greater than 3 ft, 
so you should be good. 

If the ceiling is flat and only supported by the walls, they would be 
considered  "exposed members". As long as the walls are more then 3 ft apart, I 
would assume you can use the 225 sqft.


At 09:23 AM 1/13/2012, you wrote:
>According to Table 8.6.2.2.1(a) in the 2010 ED of 13, You can space SSP's
>at 225 sq ft if "Combustible unobstructed with exposed members 3 ft or more
>on center"
>
>However, there is no mention of the same scenario minus the exposed members
>- am I missing something? This question was asked by a local guy and I
>don't guess I have a conclusive answer...
>