An Sectional Drain, although auxiliary to a Main Drain, is not an Auxiliary
Drain. An Auxiliary Drain would be like a low point drain. A Sectional
Drain is like a Main Drain for a section of a system that can be isolated
by a Sectional Valve.

On Mon, Feb 13, 2012 at 2:14 PM, Matt Mueller <m...@metrofp.com> wrote:

> I had never noticed the commentary statement "Unlike the main drain, the
> auxiliary drain is not intended to be flow tested.", but I do find that odd
> seeing that 13.3.1.2.1 of the same edition requires "When the valve is
> returned to service, a drain test (either main or sectional drain, as
> appropriate) shall be conducted to determine that the valve is open"
>  Although for that testing, it really doesn't matter the size of the pipe
> or drain, as long as there is no change from year to year, or quarter to
> quarter.
>
>
> Matthew Mueller
> Metropolitan Fire Protection
> 175 Gordon St
> Elk Grove Village
> Illinois, 60007
> P 847.758.9820
> F 847.758.9822
> C 847.602.3576
>
>
> -----Original Message-----
> From: Morey, Mike [mailto:mo...@bmwc.com]
> Sent: Thursday, February 09, 2012 12:56 PM
> To: sprinklerforum@firesprinkler.org
> Subject: NFPA 25 and main drain tests
>
> We have had a question come up about main drain testing per NFPA 25:
>
> In the NFPA 25 2011 handbook it states:
>
> 13.2.4 Before opening a test or drain valve, it shall be verified that
> adequate provisions have been made for drainage.
>
> The commentary for this item includes the phrase:
>
> In high-rise buildings with the sprinkler riser in the stairway, a
> separate drain line is often installed that is one diameter larger than the
> largest main drain valve connected to the drain line. The drain line should
> not be considered a main drain connection, but should be viewed as an
> auxiliary drain for each floor. Unlike the main drain, the auxiliary drain
> is not intended to be flow tested. The auxiliary drain line can be used to
> conduct flow tests on pressure regulating valves installed in the fire
> sprinkler system and in the fire department standpipe system, and also to
> test the system flow switch.
>
> This is followed up with the testing requirements:
>
> 13.2.5* Main Drain Test. A main drain test shall be conducted annually at
> each water based fire protection system riser to determine whether there
> has been a change in the condition of the water supply piping and control
> valves. (See also 13.3.3.4.)
>
> Additionally this annex material is presented:
>
> A.13.2.5 Main drains are installed on system risers for one principal
> reason: to drain water from the overhead piping after the system is shut
> off. This allows the contractor or plant maintenance department to perform
> work on the system or to replace nozzles after a fire or other incident
> involving system operation.
>
> The test for standpipe systems should be done at the low-point drain for
> each standpipe or the main drain test connection where the supply main
> enters the building.
>
> NFPA 13 2010 Handbook states:
>
> 8.16.2.4.5 For those drains serving pressure-reducing valves, the drain,
> drain connection, and all other downstream drain piping shall be sized to
> permit a flow of at least the greatest system demand supplied by the
> pressure-reducing valve.
>
> And the handbook expands with:
>
> Piping controlled by sectional valves represents a significant segment of
> the sprinkler system. Sectional or floor control valves serve the same
> function for that portion of the system as the main drain does for the
> entire system. The use of express drains in high-rise nuildings is one
> method of disposing of water from upper floors. Express drains or floor
> drains used when the drain does not drain directly to the outside must be
> capable of handling the flow and not restrict it.
>
> Is the NFPA 13 material meant only to apply to the full flow testing of
> pressure reducing valves? We have some concern that these two standards
> conflict on the idea of "express drains" when it comes to floor control
> manifolds not installed on combination standpipe risers. With a dedicated
> sprinkler riser is the intent to use a full flow main drain test at each
> floor control valve, or only at the lowest level of the building on the
> lead in? Floor control valves aren't explicitly defined but appear meet all
> the requirements of a "system riser" which is defined, and is the term used
> in the actual code material.
>
>
> Mike Morey, SET, CFPS
> Sprinkler Designer
> BMW Constructors, Inc.
> O: 317.651.0596 | C: 317.586.8111
> www.bmwc.com
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120209/955cf7e9/attachment.html
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120213/bc1fbd4c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to