I saw that too in section 11.1.2, but the AHJ is saying that section applies to calculations, not head placement...
Steven MacKinnon Senior Fire Protection Engineer Hartcorn Plumbing & Heating Inc. 850 South 2nd Street Ronkonkoma, NY 11779 631-580-2300 - Office 631-580-1090 - Fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richard Carr Sent: Tuesday, February 14, 2012 9:21 AM To: [email protected] Subject: Re: extending sprinkler coverage 15 feet beyond Yes you can, its in chapter 11. Steve Mackinnon <[email protected]> wrote: Hello everyone, Question, I have a janitor's closet in the middle of two locker/bathrooms, the GC didn't extend the walls of the janitor's closet to the deck leaving the deck exposed, just in the closet (finished ceilings in locker/bathrooms)... I remember a while back being told you can protect 15 feet beyond the closet without protecting the whole area above the ceiling. The building construction is non combustible and I'm using NFPA 13 2007 edition. Thanks Steven Thanks in advance for any guidance and help! Steven MacKinnon Senior Fire Protection Engineer Hartcorn Plumbing & Heating Inc. 850 South 2nd Street Ronkonkoma, NY 11779 631-580-2300 - Office 631-580-1090 - Fax [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum