Let's take this situation to where there is an engineer of record. Seems to me 
this highlights the importance of that engineer getting a feel for the water 
supply and giving to the bidding contractors the most accurate water supply 
information they can - using the information available and their engineering 
judgment. There can be a lot of variables that need consideration. The EOR 
should KNOW if a site has a radically variable static pressure; or if there is 
potential for large water use by neighboring facilities; or if a small town 
lowers its tank elevations in winter (reducing static pressures); etc.

Now for you contractors working design-build with no PE as the EOR, you are 
essentially charged with determining all of this information - and sometimes 
you are forced to fight what you know is 'right' with the demands of your 
company's pocketbook (that is, when you delve into the water supply AFTER the 
contract has been negotiated/awarded). 

But who are we kidding: most often when there IS an EOR, you are STILL charged 
with gathering this information - along with the other contractors competing 
for the job. So you better get the water supply information right - but make 
sure you're low bid, too...

BTW - it's not that you CAN'T extrapolate a flow test to higher flow than your 
test created. It's just not the best practice.  The farther away you 
extrapolate, generally, the lower the accuracy of the flow/pressure point.  So 
if you extrapolate a 2,000gpm test out to 2,100, you're probably o.k.  Just 
avoid extrapolating to 5,000gpm. Conversely, if you flow more than you're total 
demand flow, you will know that you are getting as accurate a test as possible 
(given the tools available). I have seen some engineers reject a flow test like 
I described (2,000 test for a demand of 2,100). That can be plain silly - 
especially if the retest is particularly expensive. There should always be room 
for reason... unless you're dealing with the government - then take no chances.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
[email protected] 




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jamey Prentice
Sent: Monday, April 02, 2012 2:12 PM
To: [email protected]
Subject: RE: Flow Test

That is also my take on the matter, the standard however does not appear to 
specifically require this!!! As indicated NFPA 291-2010 4.3.6 states " To 
obtain satisfactory test results of theoretical calculations of expected flows 
or rated capacities, sufficient discharge should be achieved to cause a drop in 
pressure at the residual hydrant of at least 25% OR to flow the total demand 
necessary for fire-fighting purposes." It does not require the contractor to 
use whichever demand is greater. In this case all tests achieve a drop of 25% 
as required by the standard however only one test of the three meets the system 
demand and only when using "theoretical" numbers extrapolated from the curve. 
What is to prevent a contractor from only flowing until a 25% drop in residual 
pressure has been achieved? On small dead end water mains this would be very 
easy to achieve however it would not provide a good indication of the actual 
condition or availability at the main. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of C&H Fire - Mike 
Gallello
Sent: Monday, April 02, 2012 2:40 PM
To: [email protected]
Subject: RE: Flow Test

Technically the hydrant flow test should be conducted in accordance with NFPA 
291.  It's rare anyone does it though, it's the generic static, 1 ports then 
two ports for a 3 point graph.  Look in the back of 13 for Fig A.22.3.4 for the 
idiot proof method for the flow test data.
Beyond this, in 291 there's a line (4.3.6) to flow the total demand necessary 
for fire fighting purposes.  Well, spin that into "sprinkler system demand" 
values and it's pretty simple.  Plot your 3-4 point graph depending on how many 
points you need to represent your sprinkler demand flow and get an actual 
curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons for the 
system demand was around 3000 gpm.  We had to static one as usual, but then we 
had to pop 2 separate hydrants with both 2.5" outlets to simulate the drop in 
the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply "curve"
from a static and a single residual point - you have to get enough flow out of 
the hydrants to approximate sprinkler demand flows.  At least that's my take on 
it anyway...


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamey Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: [email protected]
Subject: Flow Test

We are looking at a project that involves an addition to an existing 
Institutional occupancy(University)in Ontario Canada. Existing flow tests 
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for the 
boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose 
allowance. What flow test results should have been used for this system design? 
I  bet you can't guess what numbers the existing system has been designed too?? 
I can find nothing that requires the design contractor to use the most 
demanding curve, If test three had not been performed we would have no real 
indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can 
interpreted points on a graph such as those used in test two be used over real 
numbers such as those in test three? My gut tells me no, but it seems the 
wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to