You may also have a 25 year system life on your job, and this may not be
incorporated into the sprinkler specification.  It may be in the boiler
plate that's in the hands of the general contractor, and it may not have
been passed along to you.  I believe the sprinkler system would be one of
the elements that would have to meet this life span.  In my experience this
particular requirement is not well understood by anyone on the design side,
the contracting side, or the owner.  Whatever you do you better make it
clear what you intend to provide.  The standard "use schedule 40" may not be
applicable for aggressive water conditions if the Sched. 40 pipe won't last
25 years.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Stough
Sent: Thursday, April 05, 2012 2:43 PM
To: [email protected]
Subject: UFC3-600-01

Thanks. I had not had anyone ask about MIC in so long, I forgot about it. 
Is anyone testing for MIC and finding anything?  In the last two years,
we've tested 8 systems and only 1 had the "possibility of bacterial growth."

 
Jay Stough


________________________________
 From: "[email protected]" <[email protected]>
To: [email protected] 
Sent: Thursday, April 5, 2012 1:54 PM
Subject: RE: UFC3-600-01
 
We had a similar comment come up on a USACE project and we were allowed to
get a letter from the local fire marshal saying that there have been no
historical problems with piping corrosion in their district.

Ed
AERO Automatic Sprinkler Company
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120405/e6c0d21d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to