By default you need to calc according to 13 (which requires a full flow test). The only exception is if you use the simplified calculation method described by 13D which is essentially calculating to only a static pressure and also requires you to figure in losses through tees on the run and is only good for straight run systems (ie. tree), and mains larger than 4" (if I recall correctly).
On Wed, Apr 11, 2012 at 9:29 AM, Gary Stites <[email protected]> wrote: > If I remember right, if a 13D system is looped or gridded then, > technically, it is to be calculated against a curve rather than static > pressure, thus requiring a flow test. > > On Wed, Apr 11, 2012 at 9:20 AM, Owen Evans <[email protected]> wrote: > > > I am curious to know how many of you have had an AHJ require a full blown > > flow test be submitted with 13D calculations? 13D only requires a static > > pressure reading from the job site address. Reason being, it is > understood > > that a 13D system demand (two heads flowing, 26gpm) will not over-run a > > municipal water system. The flow test is only required for buildings that > > fall under the NFPA 13 standard. The cost of a flow test can be very > > expensive and time consuming. Contractors must wait for the water > purveyor > > to conduct the test. > > > > > > If an AHJ requires a flow test for a 13D system, and since 13D does not > > require a flow test, doesn't the AHJ have to get approval from the State > > Fire Marshal and/or Building Standards Commission to require this > expensive > > (and unnecessary) test? > > > > > > It seems to me that the only reason a plan checker would require a flow > > test for a 13D system is because they don't understand or recognize the > > reason behind a flow test. > > > > > > Any suggestions on how to educate a plan checker without making them look > > bad would be appreciated. > > > > > > Regards, > > Owen Evans > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: < > > > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/9d3529a9/attachment.html > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > -- > Gary Stites > 661-213-9379 > > RLH <http://www.rlhfp.com> > gstites.tumblr.com > Mr. Ricky <http://www.facebook.com/pages/Mr-Ricky/119445524768916> > Moondogs Golf Country Club <http://www.moondogscc.com> > NBC Worship Team <https://sites.google.com/site/nbcjudah/> > facebook.com/gsprink <http://www.facebook.com/gsprink> > Pandora Station <http://www.pandora.com/?sc=sh43464983213902734> > Hit Record <http://www.youtube.com/watch?v=beQh8jtIarM> > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/aad97cd2/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/53c3aa16/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum