The bigger question is the 15 minute thermal barrier behind a combustible 
tub/shower.  If the plans do not take into account the barrier material, 
typically drywall, it doesn't matter how small the bathroom -- sprinkler head 
required.  I typically look at the rough opening shown on the building plans.  
If the RO is 5'-00" they did not account for anything behind the tub/shower 
unit (fiberglass), that RO would have to be 5'-1".  Then figure out how the 
plumber is going to maintain that barrier when he puts in his pipes and valves.

Duane T Fox, Jr. CFPE, CFPS
Fire Protection Specialist
DE State Fire Marshal's Office


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, April 18, 2012 4:34 PM
To: [email protected]
Subject: bathrooms in dwelling units.

This may be an old controversy, but I need to get it cleared up. When 
calculating the area of a bathroom for the possible omission of sprinklers, do 
you include the area of the tub/shower? I believe you do, but this has come up 
again and I would like a clarification. 