Well, there is a lot more to it than you've brought up. First, I believe what 
you bought is a UL Listed Residential controller and a POS pump. POS stands for 
Piece of Sushi and I'm kidding on the last word. You won't see them advertised 
in SQ (Sprinkler Quarterly) because it gives people in Patterson NY heartburn 
and they won't let them mislead people. 

Didn't the State of NY learn anything about under-spec'ing sprinklers when they 
lost all those people in the 13D group home? 

Despite how it is advertised, it does meet the requirements of NFPA 13R 2007, 
so if that's your performance spec, and you bid a #20 compliant pump, any other 
bidder complying with 13R only with a POS pump would have been significantly 
less.

For the record, I'll readily admit we install a bunch of these POS pumps, 
although from a different manufacturer "Back East"  with very few troubles 
(wasn't them with the impeller problem, that was someone in St Louis). Why 
don't we use #20 pumps? Well, how many of you add a tank and pump to your city 
supplies on 13 systems? Redundant supplies are better, right? We do it because 
it is what the minimum consensus standard requires and it isn't our job to 
shove our beliefs down our customers' wallets- that's the province of the 
plumbing engineer LOL! Seriously, there are folks we'll mention it to, but the 
vast majority didn't want to spend $10 on sprinklers, let alone $10k, $30k, 
whatever. Some could elect to bid NFPA 22 compliant tanks for 13R systems which 
aren't required. Heck, we could install clean agent backup to sprinklers in I 
occupancies....that's someone's mother in that room!!!


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Justin Petcosky
Sent: Thursday, April 26, 2012 2:11 PM
To: [email protected]
Subject: RE: Automatic Fire Sprinkler Systems Fire Pumps / Aqua tanks

Thanks for your input! It is my belief this system is a falsely advertised and 
doesn't provide what was promised (That being a 13-R Acceptable Pump). 
Unfortunately this pump was required by the State of New York for an 
installation in a 13-R Residence. I from the beginning of the project stressed 
my concern about the pump not being UL listed itself and not meeting NFPA 20 
requirements. The State insisted it was okay due to the fact it was UL listed 
as an assembly. I wonder if UL knows how they are advertising this product? It 
is my belief that only the controller is the actual listed assembly. With some 
careful wording from the manufacture we now have a NFPA-13R, Listed Pump 
Assembly.  Word of advice from myself if anybody runs across this stay AWAY!!! 
TOLCO fire pumps have actual UL Listed Pumps & Controllers that meet NFPA 20. 
That was my recommendation to the State. If anybody has any other input please 
let me know!


Justin Petcosky
Project Manager/Estimator
Petcosky and Sons
Plumbing, Heating, and Fire Protection
421 Commerce Rd.
Vestal, NY 13850
www.petcosky-sons.com
607-797-0160



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, April 26, 2012 13:57
To: [email protected]
Subject: RE: Automatic Fire Sprinkler Systems Fire Pumps / Aqua tanks

If you're getting only most of the rating of the pump when testing, then you 
need to contact the mfr/supplier where you obtained it pronto and if they can't 
figure out why, get you one that performs as specified.

You might have an out if you greatly oversized the pump and you demands are met 
by the current performance. I was going to say the AHJ would have to bless the 
drop in cushion, but unless there is a local requirement, there is no minimum 
cushion in 13R, just meet the demand of the system. 

The right thing to do is to replace the unit with one performing as specified, 
the option I give is really for getting occupancy with the idea you're meeting 
code, but there's no reason for you to accept less than you bought on behalf of 
the owner, and there may be a problem that will further degrade (possibly 
quickly) performance so its best to find the cause or replace it- replacing it 
being most likely to occur, many of these 13R pumps are less than roundtrip 
plane fare to troubleshoot for the mfr. We had an impeller detach itself after 
a short installation time which was a scary thing to experience, thank heavens 
we found it in an annual not a fire, it would have been ugly and likely grounds 
for a TIA to retro-require compliance with 20 if there were enough deaths 
resulting. Course we need over 3,000 deaths to even not make enough impact in 
some circles (IRC adoption), but thankfully only one or two in NFPA (AF 
fireballs). There's an Attaboy to Shannon and Co buried in there.

Tim, don't feel bad- you may work where locals require 20 or next edition does, 
and I labored under the misconception 20 needed to be met myself for a long 
time when, at least in 2007 edition, it clearly does not. 

Roland, are you sure it was TC intent to require #20 pump when poorly written? 
It seems odd to write WHEN a fire pump is... because that clearly (to me) means 
there are times when a fire pump isn't being provided. If it was TC intent and 
they wrote what they wrote in 07 edition, then they butchered the heck out of 
it and mislead us with really bad writing.  Doubt you can blame it on the 
English majors in Quincy, either...the wordsmithers we rely on when we've spent 
three hours on a paragraph, or have an hour to get thru a chapter!


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, April 26, 2012 1:31 PM
To: [email protected]
Subject: Re: Automatic Fire Sprinkler Systems Fire Pumps / Aqua tanks

That is indeed the INTENT but if one looks at the literal text, it doesn't say 
that.  It says in 9.3  "with a pump".  It doesn't say fire pump.  Then in 9.4 
it says - where a FIRE pump is installed, it shall  
be in accordance with NFPA 20.   IF one assumes the use of pump and  
fire pump is synonymous, you get to NFPA 20.  This was cleaned up for the next 
edition such that it is explicit that the pump must a fire pump.

Roland

On Apr 26, 2012, at 6:20 AM, G. Tim Stone wrote:

> Justin,
>
> If the system in question falls under NFPA 13R then the pump needs to 
> be installed in accordance with NFPA 20.
> NFPA 20 calls for UL listed equipment. Have you contacted the pump 
> supplier for assistance?
>
> Regards,
> G. Tim Stone

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120426/4a09097d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to