To specifically answer this questions, yes, Chapter 7 Hydraulically Designed 
Sprinkler Systems, 1976 edition with light hazard and the three ordinary hazard 
curve sin Chapter 2.

Scott Futrell
 
(763) 425-1001 x 12 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Monday, May 07, 2012 6:39 PM
To: [email protected]
Subject: 1976 13 Question

Would anyone with a library know if hydraulics were referenced in the 1976 
edition of NFPA 13?
I'm going to be replacing a dry system with MIC installed in 1984 under this 
edition.  It almost looks pipe scheduled except for the main (assuming the 
schedules for LH haven't changed).  I'm assuming the 30% increase wasn't there 
either.  :P Analyzing the existing system hydraulically, I have densities in 
excess of
0.5 in the larger areas with not more than 80-90 SF per head throughout.

TD