Not related to the 1.2/1.4 topic, but on the evolution of FM datasheetd, I
just recently became aware, that as well as the Datasheets, FM also come out
with 'Engineering Bulletins' which are meant to take effect upon
publication. These Engineering Bulletins are not available on the FM
website. From what I know you have to be signed up for automatic update
notification. The recent EB 04-12  (from March 2nd), has massive impact on
use of EC spks.

Damien Shannon
Provincial Sprinkler Company Ltd.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: 21 May 2012 19:04
To: [email protected]
Subject: RE: Factory Mutual 1.2 or 1.4

FM has come a long way, baby.  As far as I've been able to tell you're on
the money, only ceiling slope bumps you to the 1.4 "shape factor".  You know
they dropped their aboveground velocity guidelines in most instances other
than that you "should" use Darcy if you're calcing over 30 ft/sec also?
There are some new restrictions that are pretty tough though, the non flat
obstructions over 4' wide rules are pretty harsh at 4' on center spacing
even in non-storage occupancies.
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: [email protected] on behalf of Brad Casterline
Sent: Mon 5/21/2012 2:02 PM
To: [email protected]
Subject: Factory Mutual 1.2 or 1.4



Before this past Saturday morning, if asked, I would have said "I don't
think FM requires 1.4 anymore, especially if it is not a high risk
occupancy". But before Friday afternoon I was not even aware of FM Data
Sheet 3-0 HYDRAULICS OF FIRE PROTECTION SYSTEMS.

On page 21, for the Density/Demand Area Format, in a nutshell it says 1.2
for ceiling slopes less than or eq. to 5 degree (1 in 12 i think), and 1.4
for slopes greater than that!

Friday I had been reading the product data of a sprinkler head that I had
seen Advertised in a mag. (be careful if FM is not the only AHJ) and I saw
the above 1.2/1.4 requirement. It was a freak coincidence to shortly realize
that it had come from FM, not the manufacturer.

Is any one aware of this? Am I just "seeing things" here? Is there more or
less to it?



thanks, 





Brad Casterline, NICET IV

Fire Protection Division



FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com



Engineering Solutions for the Built Environment



-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120521/d9044fff/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 5338 bytes
Desc: not available
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120521/50c49e57/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to