You didn't state the length of this 48"x32" reducer.

But if providing a sprinkler below creates an issue, ask for the HVAC 
contractor to just flash from the duct to the floor so there is no open space 
below.

Unfortunately there is nothing in NFPA 13 that provides for any allowances 
based on height above the floor.  It's pretty much if it's over 48" in width, 
sprinkler goes underneath. 

12" off the floor seems a bit of overkill when looking at just how much 
combustible debris could accumulate there.  Also when you look at the wording 
of NFPA 13-2010 8.5.5.3 it gives reference to the sprinkler discharge being 
limited in reaching the hazard.  If you wanted to argue the point and if the 
following is true you could state that there is no hazard present below the 
piece of duct, not enough space for storage and therefore 8.5.5.3 is not 
applicable.

It all just depends on whether it's worth the fight or not.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



On Tue, Jun 19, 2012 at 5:13 AM, Brian Harris <[email protected]>wrote:

> I have an engineer requesting I put a head under a reducer that is located
> at the floor of a mechanical penthouse. The reducer is over 48" wide at one
> end and 32" wide at the other end and is approximately 12" above the floor,
> is this really required?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/4976fd7a/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/9daae01f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to