You didn't state the length of this 48"x32" reducer. But if providing a sprinkler below creates an issue, ask for the HVAC contractor to just flash from the duct to the floor so there is no open space below.
Unfortunately there is nothing in NFPA 13 that provides for any allowances based on height above the floor. It's pretty much if it's over 48" in width, sprinkler goes underneath. 12" off the floor seems a bit of overkill when looking at just how much combustible debris could accumulate there. Also when you look at the wording of NFPA 13-2010 8.5.5.3 it gives reference to the sprinkler discharge being limited in reaching the hazard. If you wanted to argue the point and if the following is true you could state that there is no hazard present below the piece of duct, not enough space for storage and therefore 8.5.5.3 is not applicable. It all just depends on whether it's worth the fight or not. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] On Tue, Jun 19, 2012 at 5:13 AM, Brian Harris <[email protected]>wrote: > I have an engineer requesting I put a head under a reducer that is located > at the floor of a mechanical penthouse. The reducer is over 48" wide at one > end and 32" wide at the other end and is approximately 12" above the floor, > is this really required? > > Brian Harris, CET > BVS Systems Inc. > Sprinkler Division > bvssystemsinc.com<http://bvssystemsinc.com/> > Phone: 704.896.9989 > Fax: 704.896.1935 > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/4976fd7a/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120619/9daae01f/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum