Then you can use a head that is UL Listed QR/FM SR to comply with NFPA and FM, correct?
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matt Grise Sent: Thursday, June 21, 2012 7:30 AM To: [email protected] Subject: RE: FM extended coverage concealers? Table 3 in FM 2-0 lists spacing allowed for quick and standard response heads in hazard category 1, so I am guessing they allow both. Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, June 21, 2012 9:21 AM To: [email protected]; [email protected] Subject: RE: FM extended coverage concealers? Matt, Does FM require QR sprinklers in LH? Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of ParsleyConsulting Sent: Thursday, June 21, 2012 6:42 AM To: [email protected] Subject: Re: FM extended coverage concealers? Matt, Based on what I saw on their website this morning they don't have and EC concealed which is approved. They have a good number of recessed EC sprinklers in both light and ordinary hazard applications, but no concealed. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [email protected] <mailto:[email protected]>e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website On 6/21/2012 5:21 AM, Matt Grise wrote: > The last time I looked FM did not allow extended coverage concealed sprinkler > heads... is that still the case? > > If not, what EC concealer has gotten an FM listing? > > Thanks, > > Matt Grisé PE*, LEED AP, NICET II > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS& MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum