I like the foreign material on the system argument. If we can call out
telephone wire aqnd suspended safes why not frisbees?

On Thu, Aug 2, 2012 at 9:55 AM, Cahill, Christopher <[email protected]>wrote:

> I'd flag it under NFPA 25 '10 - 5.2.1.  Plenty in there like foreign
> materials or in the wrong orientation (because the plate implies it's too
> far down from the actual ceiling and should be upright based on the BL
> location, OK, maybe that's weak).  You have no idea if it was AHJ approved
> condition before you got there.  If you do as Ron suggested I'd use 5.2.1
> as you did a deficient inspection as that section tells you exactly what to
> look for at the sprinkler, there is foreign material hanging from part of
> the sprinkler.  Don't get me wrong I see where Ron is going for other
> things that are not mentioned like suspected small pipe size, incorrect
> density and incorrect spacing.
>
> Not sure I agree with Steve's using of the critical definition generically
> as a trump card for everything.  First, some other section must identify
> what you are looking for then you'd use the definitions to establish an
> impairment, critical or non-critical deficiency?  Is this a deficiency?
>  Yes under 5.2.1.  Is it an impairment, no.  Is it a deficiency? Yes but I
> don't know which level as I don't have details. Short room you are probably
> in the jet and it won't make a difference.  Tall space you may be in the
> plume and might make a bigger difference.  In the end I'd never put my name
> on it as OK.
>
> What did you mean they were accepted?  Just because an ahj agreed doesn't
> mean they were ever acceptable by the code.  And many moons ago I'm sure
> there were plenty of AHJ that said no.  I seem to only have come across in
> places that have limited oversight.  I've seen them on system's installed
> in the last 5 years.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, August 02, 2012 11:26 AM
> To: [email protected]
> Subject: Re: NFPA 25 inspection of sprinklers with heat collector plates
> installed
>
> Gregg,
>
> I'd make one of those "not part of the inspection" comments, but an area
> of potential concerne and do the "recommendation of an engineer's review."
>
>
> On Thu, Aug 2, 2012 at 9:23 AM, Gregg Key <[email protected]> wrote:
>
> > Forum, if you were inspecting a building and found some pendant
> > sprinklers with the "heat collectors" installed, would you write it up
> > as a deficiency and why?
> >
> > Many moons ago they were accepted but later research proved they did
> > not work.
> >
> > C.Gregg Key, SET
> > Key Fire Protection Services,Inc
> > Project Manager
> > (O) 706-790-3473
> > (C) 706-220-8821
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120802/ac39cc84/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120802/52ef1513/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to