Imagine adding up all the years of experience, in various locales and different 
points of view (contractor, AHJ, mfrs, insurance, FPEs, etc) that are applied 
to situations like yours?
P R I C E L E S S 

Makes the membership dues of AFSA seem trivial in comparison....yes, it's that 
time of year. Although my health precludes me from flying at this time, I'd 
urge all of you to consider attendance at AFSa's convention, and membership if 
you haven't.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
rfletc...@aerofire.com
Sent: Monday, August 27, 2012 9:45 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Supervised vales in pump room

My thanks to everyone for the information. This forum is awesome.

Ron Fletcher
Aero - Phoneix

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Monday, August 27, 2012 4:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Supervised vales in pump room

And...

NFPA 20 2010:4.16.2 Supervised Closed. 
The test outlet control valves shall be supervised closed.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, August 27, 2012 7:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Supervised vales in pump room

If leaving the valve in the wrong position will impair the operation of the 
sprinkler system, then the valve must be supervised, see below.

NFPA 101 2012:9.7.2.1 Supervisory Signals.  
Where supervised automatic sprinkler systems are required by another section of 
this Code, supervisory attachments shall be installed and monitored for 
integrity in accordance with NFPA 72 , National Fire Alarm and Signaling Code, 
and a distinctive supervisory signal shall be provided to indicate a condition 
that would impair the satisfactory operation of the sprinkler system. 
Supervisory signals shall sound and shall be displayed either at a location 
within the protected building that is constantly attended by qualified 
personnel or at an approved, remotely located receiving facility.

Also...

IBC 2012:903.4 Sprinkler system supervision and alarms. 
All valves controlling the water supply for automatic sprinkler systems, pumps, 
tanks, water levels and temperatures, critical air pressures and waterflow 
switches on all sprinkler systems shall be electrically supervised by a listed 
fire alarm control unit. 

Exceptions: 

1. Automatic sprinkler systems protecting one- and two-family dwellings.
2. Limited area systems serving fewer than 20 sprinklers.
3. Automatic sprinkler systems installed in accordance with NFPA 13R where a 
common supply main is used to supply both domestic water and the automatic 
sprinkler system, and a separate shutoff valve for the automatic sprinkler 
system is not provided.
4. Jockey pump control valves that are sealed or locked in the open position.
5. Control valves to commercial kitchen hoods, paint spray booths or dip tanks 
that are sealed or locked in the open position.
6. Valves controlling the fuel supply to fire pump engines that are sealed or 
locked in the open position.
7. Trim valves to pressure switches in dry, preaction and deluge sprinkler 
systems that are sealed or locked in the open position.


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research Services 
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com]
Sent: Friday, August 24, 2012 1:36 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Supervised vales in pump room

I'm not sure NFPA #25 would apply to a new installation. NFPA 20 requires the 
pump enclosure to be supervised or controlled but I found nothing requiring 
valve supervision. I don't have access to the codes on line right now so I 
can't look it up without going old skool using a book and that's too much 
trouble for Friday. I think IFC requires supply valves to be supervised.

Ron Fletcher
Aero - Phoenix

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Morey, Mike
Sent: Friday, August 24, 2012 10:21 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Supervised vales in pump room

There is no blanket requirement, NFPA 25 2010 4.16 covers what valves must be 
supervised, personally I think it's rather poorly worded, but if you read 
through the whole standard my impression is the intent of 4.16.2 Supervised 
Closed. The test outlet control valves shall be supervised closed. includes 
these valves, otherwise you could leave the meter bypass open and have no 
pressure.  Typically we'd lock a valve like this open.  One could argue that 
the test outlet control valve is defined as the test header control valve, but 
there's a checklist in the standard that makes mention that test header AND 
meter bypass valves need to be supervised (form S2.2).  
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: sprinklerforum-boun...@firesprinkler.org on behalf of 
rfletc...@aerofire.com
Sent: Fri 8/24/2012 1:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Supervised vales in pump room



Here is an easy one for Friday. Is there a general requirement that all valves 
in a pump room be supervised? I am wondering about the valves in a flow meter 
loop that are normally closed.

Ron Fletcher
Aero - Phoenix
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4502 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120824/ac3913a2/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to