That section only applies to combined systems.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Morey, Mike [mailto:[email protected]] 
Sent: Tuesday, September 04, 2012 9:43 AM
To: [email protected]
Subject: RE: drum drip in cold spaces

NFPA 13 2010 says:
7.4.4.4 Section drain lines and dry pipe system auxiliary drains shall be 
located in heated areas or inside heated cabinets to enclose drain valves and 
auxiliary drains for each section.

That said we typically insulate and heat trace them with a supervised heat 
tracing, I don't believe what we use is actually UL listed for fire protection 
but we haven't had any issues come up from it.

 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: [email protected] on behalf of Todd Williams
Sent: Tue 9/4/2012 9:25 AM
To: [email protected]
Subject: drum drip in cold spaces



I am working on a dry system where we have to install some drum drips. However, 
they will be installed in the cold spaces (outside, not cooler/freezer). Do 
these need to be protected from freezing? Any suggestions how?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4441 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120904/d42e392c/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to