Ok
then that leads to nfpa 13 with quick response sprinkler and room design method 
@ 0.1 density  or could that qualify under the exception  residential fire 
loading of 13R outside the dwelling



 
-----Original Message-----
From: Steve Leyton <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Wed, Sep 19, 2012 11:07 am
Subject: RE: Basements storage in multiple dwellings


Basements that are not used as a dwelling unit in a conforming
esidential building are addressed in NFPA 13R, 7.2 Design Criteria -
utside Dwelling Unit.
The foregoing is my opinion only and does not necessarily represent the
pinion or intent of the NFPA 13D/13R Technical Committee on Residential
prinkler Systems.
Steve Leyton
rotection Design & Consulting
an Diego, CA

----Original Message-----
rom: [email protected]
mailto:[email protected]] On Behalf Of
[email protected]
ent: Wednesday, September 19, 2012 6:54 AM
o: [email protected]
ubject: Basements storage in multiple dwellings

an 13R be used in a common storage area basement  a multiple dwelling.
s the Basement considered part of dwelling if it is used as accessory
torage to dwelling section 6.2.2 of 13 R permits residential sprinklers
n certain areas with similar fire loading

------------- next part --------------
n HTML attachment was scrubbed...
RL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ents/20120919/ac602e51/attachment.html>
______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120919/53f1c60f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to