I suspect that your confusion stems from assuming that the required K-11.2 forces you to go to section 16.2.2. There are Large Drop sprinklers with a K-11.2 and spray sprinklesr with a K-11.2. So yes you can stay with the control mode density. You can also go to a larger K-factor and save some pressure (such as going to a K-16.8)

Roland

On Sep 20, 2012, at 1:10 AM, Andrei Titel wrote:

I'm new in using NFPA 13 and I would appreciate your
help for the following matter:


For class IV rack storage according to NFPA 13 I have
two options to design my sprinkler system:
-control mode density area
-large drop sprinklers and specific application
control and mode sprinklers.

According to table 16.2.1.3.2 I have to use fig
16.2.1.3.2(d) curve E. For me to reach sprinkler density I must use ELO
sprinkler K 11.2.

My question is: can I still use control mode density
or do I have to use large drop application, because according to table
16.2.2.1 for K 11.2 sprinkler the minimum sprinkler operating pressure is 3.5
bar for class IV.

This is an existing system and the pump can't deliver
that much pressure.

Thank you.