Hi Scot.
Could you explain what do you mean with Ergo named S.A.?

C.L.R. 


-----Mensaje original-----
De: [email protected]
[mailto:[email protected]] En nombre de å... ....
Enviado el: jueves, 20 de septiembre de 2012 03:34 a.m.
Para: [email protected]
Asunto: Sprinkler design for class IV rack storage

Andrei:

You might be able to avoid a pump if you go in-rack.  but your client
probably will experience a broken in-rack sprinkler   in their future
operations, and be quite upset.

Special application sprinklers usually offer an advantage by reducing the
demand for  pressure-volume work (i.e. pump size), ergo their name "SA".

Control-mode, ceiling-only will probably demand a bit more  pressure-volume
work from your source, but the sprinkler might be a bit less expensive that
SA.

Since you are attempting to design a sprinkler system without having to
replace a fire pump, it appears you will need to pursue each option and see
what the demand is, relative to the supply your pump offers.  There are
slight improvements that can be made to pump performance, based upon
changing out impellers, but that is only if the demand is close to the
pump's current supply capacity.


There is no single 'best' answer.  You, as designer need to weigh your
variables and make a judgment (and describe the rationale) for the
stakeholders as to why you choose what you chose.



scot deal
excelsior fire
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120920/1bef6c88/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to