You can lead an AHJ to water but you can't make him think. Or see what you 
think is obvious.
Might want to print out responses from the Forum and show him what your peers 
say and cite (save this for when he still says No). 

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Saturday, September 29, 2012 2:52 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler head Temperature requirement

All said and done, I think it's pretty clear that the intent is to allow the 
use of those sprinklers.
 
SL

________________________________

From: sprinklerforum-boun...@firesprinkler.org on behalf of mphe...@aerofire.com
Sent: Sat 9/29/2012 11:39 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement



The 2002 version of 8.3.2.3 differs from 2010 only by the inclusion of 
"intermediate temp" in the text. The "store" will be display in room style 
settings, no "storage". The roof is at 27 feet and is a panelized wood 
structure with open web wood joist on 8' centers, and I agree with you on the 
benefit of the 286* F sprinklers providing better performance.
Mark at Aero

----- Original Message -----
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Saturday, September 29, 2012 10:14 AM
To: sprinklerforum@firesprinkler.org <sprinklerforum@firesprinkler.org>; 
sprinklerforum@firesprinkler.org <sprinklerforum@firesprinkler.org>
Subject: RE: Sprinkler head Temperature requirement

At home this morning and don't have the 2002 NFPA 13 laying around, but it may 
be that if the older standard doesn't include the conditional application 
granted in 8.3.2.3 (2010 ed.) then he or she is holding you to the letter of 
the 2002.  You might want to point out that the intent of any TC can generally 
be found in the latest edition of a standard.  

When you say furniture retail, is this going to be a showroom only, with the 
sales floor done up as "rooms" for display only?  Or will there be an area for 
storage as well, and what fire load overall do you anticipate?   Seems to me 
that even a moderate load of furniture can still generate a pretty high release 
of energy and the 286 sprinklers (as Ron mentioned, I think) may well respond 
more symettrically.   What is the height of the deck above and what's it framed 
with?

SL

________________________________

From: sprinklerforum-boun...@firesprinkler.org on behalf of mphe...@aerofire.com
Sent: Sat 9/29/2012 5:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler head Temperature requirement



What we have is High temp heads installed in an ordinary hazard occupancy. I 
believe 8.3.2.3 does explicitly allow this. The inspector has a different 
opinion. My position is 8.3.2.3 doesn't leave room for opinions, and wasn't 
intended to!
Mark at Aero

----- Original Message -----
From: Bruce Verhei [mailto:bver...@comcast.net]
Sent: Saturday, September 29, 2012 12:47 AM
To: sprinklerforum@firesprinkler.org <sprinklerforum@firesprinkler.org>
Subject: Re: Sprinkler head Temperature requirement

Mark

My understanding of this is to ensure that ordinary temp heads are replaced 
with at least intermediate heads are installed to prevent head operation in 
absence of a fire.

Bv

Sent from my Motorola ATRIX(tm) 4G on AT&T

-----Original message-----
From: Roland Huggins <rhugg...@firesprinkler.org>
To: sprinklerforum@firesprinkler.org
Sent: Fri, Sep 28, 2012 22:40:08 GMT+00:00
Subject: Re: Sprinkler head Temperature requirement

as Todd already said, it is explicitly allowed by 8.3.2.3 unless the AHJ is 
trying to call it a light hazard occupancy.

Roland

On Sep 28, 2012, at 10:00 AM, <mphe...@aerofire.com> <mphe...@aerofire.com > 
wrote:

> I have a Friday question for the forum, and maybe Roland is able to > respond 
> with some "intent" perspective. In a 27' high industrial  > spec building, we 
> installed sprinkler heads rated at 286 degree. > This was permitted, 
> installed, inspected and approved. The owner now > has a tenant lease which 
> will build out the entire building as a > retail furniture showroom, no 
> ceiling and no storage. The local fire > inspector is siting NFPA 2002 
> Edition section 8.3.2.2,  "Where > maximum ceiling temperatures exceed 100 
> degrees F, sprinklers with > temperature ratings in accordance with  the 
> maximum ceiling > temperatures of Table 6.2.5.1 shall be used." , as a 
> requirement to > remove all the sprinklers in the building and replace them 
> with 212 > degree F sprinklers.  My contention is that the next section,  > 
> 8.3.2.3 "High temperature sprinklers shall be permitted to be used > 
> throughout ordinary and extra hazard occupancies and as allowed in > this 
> standard and other NFPA codes
 and standards.", allows the > existing 286 degree sprinklers to remain and be 
in compliance with > NFPA 13. What say the professionals, Roland, Steve, 
George, Ron, > Rod, Anyone .....?
> Mark at Aero
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120928/c513f5a8/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120929/bf582009/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 7399 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120929/f87ea66e/attachment.bin>
_______________________________________________