I have a situation where the GC wants to change the new sheet rock ceiling system to a walk-able hard ceiling. We're talking about a room 17 ft x 29 ft, with one 24"x24" access panel. This would create a room above a room... The purpose of this is to allow for future maintenance of filters and mechanical equipment.
Would this be considered a concealed space and fall under section (NFPA 13 2007 ed.) 8.15.1.2.2 and not have to be protected or is it considered a separate room and will require sprinkler heads? Thanks in advance... Steven MacKinnon Senior Fire Protection Engineer Hartcorn Plumbing & Heating Inc. 850 South 2nd Street Ronkonkoma, NY 11779 631-580-2300 - Office 631-580-1090 - Fax [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum