Curious on the addition of balconies.  It has been that way (without balconies) 
in 13R for 20 years...what caused the change now?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Friday, October 12, 2012 9:34 AM
To: [email protected]
Subject: Re: 13R balcony protection

The 2009 edition of the IBC added the balcony must have a roof or deck above 
regarding required sprinkler protection.  Nothing regarding whether the 
overhang on the top floor is a driver.  Additionally, the
2013 edition of NFOA 13R finally acknowledge the supremacy of the code over 
standards in driving such matters and added the below text.


6.6.5* Except as provided for in 6.6.5.1, sprinklers shall not be required in 
any porches, balconies, corridors, carports, porte cocheres, and stairs that 
are open and attached.

6.6.5.1 Where a roof or deck is provided above, sprinklers shall be installed 
to protect attached exterior balconies, attached exterior decks, and ground 
floor patios serving dwelling units in buildings of Construction Type V.

6.6.5.1.1 Where sidewall sprinklers are installed beneath decks or balconies 
constructed with open wood joists, sprinklers shall be permitted to be 
installed with deflectors not less than 1 in. (25 mm) or more than 6 in. (152 
mm) below the structural members, provided that the deflector is not more than 
14 in. (356 mm) below the underside surface of the deck. systems, or other 
reliable means capable of maintaining a minimum temperature between 40°F and 
120°F (4°C and 48.9°C).

Roland




On Oct 8, 2012, at 4:50 AM, Todd Williams wrote:

> The Connecticut Fire Safety Code (at least the part that is based on 
> the IFC) includes a requirement that exterior balconies and patios be 
> sprinkelred in 13R occupancies. However, this is being interpreted 
> that they have to be protected regardless if there is any structure 
> above or not. Consequently, we have to install sidewall sprinklers 
> under 9" door moldings because they open on to a patio or deck (just 
> got a plan rejected for this). This make no sense to me because they 
> would most likely never activate, but this is being enforced as the 
> law. Anybody else run into this?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121012/502a72f6/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to