Be sure to check the air water solenoid on these valves, we have had issues 
with these. They do not operate like a typical dry pipe. There was also a recal 
that applied to certain pin assemblies on the check!

Regards,
Jamey

On 2012-10-25, at 12:15 PM, "Gregg Key" <[email protected]> wrote:

> Very good feedback. This system was installed in 2006 and is a Victaulic
> dpv. We have none of the original acceptance test paperwork but would make
> an assumption that it would have passed then. It appears to be a small
> system. Mike ,you are right about the by-pass line as it appears that there
> is not one installed. Air Compressor is in a hidden crawl space below the
> floor. My thought was that something has restricted the air release in the
> inspectors test but have not taken it apart. Thanks for everyones help 
> 
> C.Gregg Key, SET
> Key Fire Protection Services,Inc
> Project Manager
> (O) 706-790-3473
> (C) 706-220-8821
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Mike Cabral
> Sent: Thursday, October 25, 2012 10:40 AM
> To: [email protected]
> Cc: [email protected]
> Subject: Re: trip time per nfpa 25
> 
> I would check to make sure that the air supply to the DPV is working as it
> should. The time to trip should never be that long. Is the by-pass open?
> Sounds like the make-up air is supplying to much air. The make up air needs
> to be restricted. The supply line to the Inspectors Test can be larger than
> 1" it can't be less than 1" however the standard does no say it can't be
> larger than 1". 
> 
> Sent from my iPhone
> 
> On Oct 24, 2012, at 1:13 PM, Todd Letterman <[email protected]> wrote:
> 
>> It is also not going to trip or be severely delayed if there is a water
> column occurrence holding the clapper shut.  
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Ron 
>> Greenman
>> Sent: Wednesday, October 24, 2012 11:06 AM
>> To: [email protected]
>> Subject: Re: trip time per nfpa 25
>> 
>> I don't believe their is any reference to "how long is too long" 
>> except in
>> 13 (pre 2010) where a system of between 500 & 750 gallons is required to
> have a QOD if the water delivery time to the inspectors test exceeds 60
> seconds. I think there is a presumption that a system of less than 500
> gallons will trip in a "timely" manner, that over 750 gallons won't without
> a QOD, and that in between one is questionable. From there the one minute
> trip time came to be the conventional standard, although the book only
> referred to water delivery time after the trip occurred. In the 2010 edition
> times are specified. See section 7.2.3.6 Dry Pipe System Water Delivery.
> Although entitled as "water delivery time" it tells you that the delivery
> time countdown starts at normal air pressure which suggests pre-trip, tto
> the actual trip, and finishing with water at the test port.
>> 
>> On Wed, Oct 24, 2012 at 10:27 AM, Gregg Key <[email protected]> wrote:
>> 
>>> Our inspector ask an interesting question today. How long is too long 
>>> of a time for a dry valve to trip before it is considered a 
>>> deficiency? 25 does not specify but 15 min seams too long. Don't have 
>>> the previous report to compare it to.
>>> 
>>> C.Gregg Key, SET
>>> Key Fire Protection Services,Inc
>>> Project Manager
>>> (O) 706-790-3473
>>> (C) 706-220-8821
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis 
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> -------------- next part -------------- An HTML attachment was 
>> scrubbed...
>> URL: 
>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
>> chments/20121024/57fe47b6/attachment.html>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to