Sorry so late. A couple of years ago I ran across some defective ball valves 
which I discovered only because of an unusually long trip time. The inside of 
the casting was horrible and caused the valve to destroy itself preventing it 
from opening completely.

--- Original Message ---

From: George Church <[email protected]>
Sent: October 25, 2012 10/25/12
To: [email protected]
Subject: RE: trip time per nfpa 25

I'd call it a revenue opportunity. Visors would help trip time, but if a water 
delivery calc indicated a higher air pressure decreased transit time as well, 
then you have a method of reducing possibly two of the two variables- trip time 
and transit time- with a little money spent on the FDT program and some elec 
accelerators.  FTD could also tell you what piping needs to be changed in order 
to enhance transit time, so that you're not just slapping on a second DPV next 
to each and splitting systems with the results only available after the 
installation and after all that money os spent- to see if it works or not? 
That's similar to installing a grid and calcing it afterward- or in the early 
stage, not calcing it but putting pie pans down on the floor, to see if the 
sizes were right.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Wednesday, October 24, 2012 2:32 PM
To: [email protected]
Subject: RE: trip time per nfpa 25

From old time experience there may be obstructions at the dry inspector's test 
valve or other that is obstructing the flow of air. From insurance inspector 
days anything over 3 minutes needs further investigation. I would have called 
15 minutes a failure in the 60's and 70's.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregg Key
Sent: Wednesday, October 24, 2012 1:27 PM
To: [email protected]
Subject: trip time per nfpa 25

Our inspector ask an interesting question today. How long is too long of a time 
for a dry valve to trip before it is considered a deficiency? 25 does not 
specify but 15 min seams too long. Don't have the previous report to compare it 
to. 

C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5351 - Release Date: 10/24/12

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5351 - Release Date: 10/24/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to