I agree that you would have to follow NFPA 13/15 hanger requirements for 
spacing of pipe stands you are building to support pipe around like a pump set 
or a transformer. In the pipe rack however I think you can only use what you 
are given. In the past we have used flanges to join bulk pipes in the rack. 
Threaded branchlines hold up okay with hangers every 20 ft. Of course we did 
all of this back before the scientists got involved in NFPA 13 so if it was 
solid, wouldn't wiggle if pulled on, didn't fall down from its' own weight and 
didn't move when flow tested it was good enough.

Ron Fletcher
Aero -Phoenix

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 7:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports

Whether it's a pipe stand, a hanger or pipe rack, they must conform to the 
spacing requirements of the applicable standard.  NFPA 15(2012) 5.6 defers to 
NFPA 13 for hangers.  I can't find any A10.4.1 in NFPA 15, 2012.  

So no, 20' hanger spacing is not compliant with the NFPA 13 or NFPA 15 
standards.  The assertions of the structural engineer are incorrect.

Additionally,  I would suggest looking at the installation manuals provided by 
the coupling manufacturers to see if they refer to any particular support 
spacing requirements if there is specific direction needed.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Hinson, Ryan
Sent: Tuesday, November 06, 2012 7:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe support spacing requirements for structural supports

I've got a couple projects which have pipe racks for supporting above grade 
firewater piping.  These rack supports are spaced at 20' or more on center.  
From the NFPA 13 Handbook at the beginning of Chapter 9, pipestands are to have 
the same safety factors as hangers.  NFPA 15 is suggested for additional 
guidance.  NFPA 13 limits hanger spacing to 15'.  NFPA 15 (2012) Sections 
6.3.2.2 and 6.3.2.3 state that firewater piping shall be supported under fire 
conditions and shall be supported from steel or concrete structural members or 
pipestands.  "Do these also need to conform to the 15 ft maximum spacing?"

I've received this question from a structural engineer regarding the pipe 
support requirements for NFPA 13 (2010) Chapter 9.  His assertion is that this 
refers to pipe stand and pipe hanger spacing requirements for piping 8" and 
smaller only.  As such, his feeling is that there are no limits on spacing for 
concrete and steel support conditions other than those required per AWWA M11 
4th Edition Chapter 7 and sound structural engineering design.  Incidentally, 
NFPA 15 (2012) Section 6.3.2.2 calls out structural supports specifically as if 
there is some difference for their design and does not actually provide a limit.

Both NFPA 20 (2010) Section 4.13.5 and NFPA 24 (2010) Section 12.1 state above 
ground piping and fittings must comply with NFPA 13 regarding hangers and 
supports.

NFPA 15 Section A.10.4.1 refers to AWWA M11 as applicable for installation of 
pipe and fittings.

NFPA 15 Table 6.3.2.2.2 only goes up to 8" pipe.  AWWA M11 has some pipe 
support requirements for steel piping.  At first glance, they do not appear 
applicable for fire water systems as they are not specifically included in 
Chapter 1 Uses.  Chapter 7, Supports for Pipe, states the load is determined to 
be the weight of the water filled pipe.  NFPA 13 requires the load to be 5 
times the weight of the water filled pipe (see Section 9.1.1.2(1)).  The 5 
times load factor seems to be only applied to hangers and stands as well, 
applying this to steel and concrete supports would be too conservative.  It 
appears the design of the steel and concrete supports would be covered by AISC 
13th edition, ASCE 7-05, and ACI 318 codes.

As an example to the above difference:  See 8" Schedule 40 pipe (this is 
standard weight pipe).  The wall thickness is .322 inches.  Per AWWA M11 Table 
7.1, this approximately nominal 5/16" wall thickness can have supports 45 ft 
apart.  8" schedule 10 (3/16" wall thickness) can be spanned up to 38' 
according to this table!  I'm not up on the nuances of piping and deflection 
but I believe the intent is to provide considerable safety into the supports of 
all types for firewater related piping.

Is it the opinion of the forum that 15' along with the allowable extensions per 
NFPA 15 is the maximum or are we to use structurally designed supports at their 
stated allowable spans for supporting this piping?  What say you?

Ryan L. Hinson, EIT, SET
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell 
Minneapolis-St. Paul Office
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-3662
Fax: 952-229-2923
rhin...@burnsmcd.com
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud recipient of PSMJ's Premier Award for Client Satisfaction

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121106/24d34187/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to