Are you allowed to fill CPVC pipe-work with compressed air? Check it out.

-----Original Message-----
From: Jim Davidson [mailto:[email protected]] 
Sent: 14 November 2012 21:09
To: [email protected]
Subject: RE: CPVC leak

Be very careful about introduction of a foreign substance into a CPVC pipe 
system, need to check if the odorant is compatible with CPVC piping. You do not 
want to introduce a substance that could cause environmental stress cracking. 
If you do, you have just brought the system.

Regards

Jim    

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Wednesday, November 14, 2012 2:16 PM
To: [email protected]
Subject: RE: CPVC leak

Did the owner who drained it note anything about the leak? Is there any 
evidence of water/glycerin staining?

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Johnson
Sent: Wednesday, November 14, 2012 1:09 PM
To: [email protected]
Subject: CPVC leak

Need some input:  Working on an existing CPVC system which original owner 
drained glycerin out of the system because of a leak.  We have tried to find 
the leak with 40 psi of air pressure, still unable to find a leak.  Has anyone 
introduced a smell into the system with the air pressure to find such a leak.  
If so, what could we use for the smell?

 

    Steve Johnson

Office:801.295.1189

  Fax: 801.295.1193

  Cell: 801.301.3950

 

     www.chpfire.com

   

 
<http://www.google.com/search?q=chaparral+fire+protection+&ie=utf-8&oe=u
tf-8&aq=t&rls=org.mozilla:en-US:official&client=firefox-a>
<http://www.facebook.com/pages/Chaparral-Fire-Protection/110753688988876
> 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 14568 bytes
Desc: image001.png
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 959 bytes
Desc: image002.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 937 bytes
Desc: image003.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment-0001.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to