Flow and pressure are related, as you stated below. Most of the time you will 
start with a known flow which is based on your density and sprinkler area. 
However, there are portions of code and/or manufacturer's requirements that 
start off with a required pressure. 

Duane

----- Original Message -----
From: Jeff Garrison [mailto:[email protected]]
Sent: Wednesday, November 14, 2012 03:02 PM
To: [email protected] <[email protected]>
Subject: Re: flow per sprinkler

Flow depends upon pressure, your calculated numbers are corrrect...


On Wed, Nov 14, 2012 at 2:40 PM, Rubén Miranda Idrovo
<[email protected]>wrote:

>
>
> Hi evreybody:
> I¨m new in the sprinklers world so I have a question every sprinkler
> (ESFR, CMDA, CMSA) have a fixed flow value (GPM) no matter the pressure???
> or the flow is up to the pressure value???
> for example an ESFR k 16.8 according to the "k" formula k=Q/ P^(1/2)
> with 64 PSI flow will be 134.4 GPM
> with 50 PSI flow will be 118.7 GPM
> Is this right???
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/d1c5ed0c/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/da227ed4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to