Todd,


Most likely the pressure would be about 150psi, reducing for a fire location 
below the valve or increasing for a fire above the valve.



(pressure loss due to height  P= 0.434 x h)



Here is an excellent paper on the subject: 
http://www.haifire.com/Resources/publications/RFFireHoseFrictionLoss.pdf



As for waiting for water,  a properly installed accelerator device will open 
the DPV quickly and by having the nozzle of a 1-1/2" hose open the air will be 
displaced quickly by the incoming water or if it's a class three stand pipe, 
just open the 2-1/2 valve until you have a steady stream of water flowing.



Yours truly,

Capt. Frank J. Herrick