Most DPV's that I'm aware of have the main drain below the wet seat. Therefore allowing a main drain test without tripping the DPV.
-Bill
On 12/28/2012 8:49 AM, Todd Williams wrote:
Vince,

You may not find the 2" drain on the dry system worthless after a trip test and it 
may be advantageous to pipe it to the outside wall (even if partially trapped). That 
being said, from what my understanding is that the 2" drain test is to verify that 
the valves are open and that by comparing results year over year, you can detect changes 
in water supply. Those can be pretty much done from  a test at the main riser , with the 
exception of the valve for the dry system.  The AHJ will probably be the determining 
factor.




At 09:38 AM 12/28/2012, you wrote:
Good morning & Happy New Year!

A 2" main drain test is required for system acceptance.

We're installing a dry pipe valve downstream and
auxiliary to a wet system with an alarm valve and a 2" drain.

My question is , would a 2" main drain test from the existing wet
system stand for an acceptance test or do we have to find a way
to run a worthless 2" drain line from the new dry system (at an inside wall)
to an outside wall?

Thanks!                                       Vince


Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136       440 238-4800     Fax 440 
238-4876

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121228/cd9959bc/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to