Look at 2.3.6.5on pgs 52-53 of FM DS 8-9.  One level IRAS at 5' OC and lower 
the roof storage height to whats shown. A lot easier to protect, and allows up 
to 20' clear. After 20', false ceiling, Equivalency FPE, etc. none of which are 
pretty. 

Assuming AHJ would allow specific FM DS criteria since 13 doesn't. I've rarely 
had a problem. Lots of solutions out there without the blessings of the 13 TC 
and the delay in getting adopted- both in the standard and in your hometown. 
Could u use ATTIC heads if you're under 1989 13 since they weren't out until 
92? On basis of superior performance )vs SSU), itd be stupid to ignore a better 
answer. Ok, badge-heavy sound better than stoopid?


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne Martinez
Sent: Thursday, January 03, 2013 10:58 AM
To: SprinklerFORUM
Subject: Ch 17 NFPA 13 (07ed)

What happens when the clearance from the ceiling to storage exceeds 10ft for 
rack storage of plastic?  Is this outside the scope of NFPA 13?

 

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130103/8f0de086/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to