I'd say you need to include the house because you're tapped off a dead end
line, not a loop, and the domestic demand of the house becomes a part of
the total flow along that feed line. As Jamie said you will have to pipe
the domestic to the house from downstream of  the domestic outlet on the
shut-off device. A pump may be a more economical solution presuming you
need to shut off domestic flows due to pressure drop rather than excessive
consumption.

On Thu, Jan 17, 2013 at 8:12 AM, Charles Thurston <[email protected]>wrote:

> Hello IPA,
>
> The way the Tyco valve works is:
>
> Looking at the cut sheet ONLY the 2" valve is listed for 12R.
>
> When there is no back pressure on the sprinkler outlet it diverts all the
> water
> that direction cutting off the flow to the domestic port.
>
> When the pressure on the sprinkler outlet builds up to the supply pressure
> it
> opens the port to the domestic port.
>
> When the pressure on the sprinkler port drops it closes off the domestic
> port.
>
> How are you going to handle domestic cutoff for the other buildings when
> one of
> them has a fire flow?
>
> These valves will not trigger domestic cutoff unless the pressure on the
> sprinkler port of THAT valve drops.
>
>
> The only way "I See" to make your situation work put one of these valves
> at the
> meter.... Run a line from the domestic port to ALL the buildings for
> domestic
> supply AND run a line from the sprinkler port to ALL the buildings for the
> sprinkler....
>
>
>
>
>
>
> Thursday, January 17, 2013, 9:49:31 AM, you wrote:
>
> > Hey,
>
> > I have an existing home with a new structure going up with 4 apartments
> all
> > on the same lot. Apartments are going to be per 13R. The existing house
> is
> > not sprinkled and not required to be at this time. The water for the
> house
> > and the apartments are being supplied via the existing water line and
> > meter. The new apartments will tap into the shared line right past the
> > existing meter. Using 3.0 k-factor sprinklers I can make the system work
> in
> > this configuration but I will need to use Tyco's automatic domestic
> shutoff
> > valves in order to avoid factoring in the domestic draws and exceeding
> the
> > gpm limitations of the water meter. When the water line enters into the
> new
> > apartment building it tees off to the domestic and the other end of tee
> is
> > for fire.
>
> > Question is: Besides the obvious location of the automatic domestic
> shutoff
> > valve within the apartment building will an additional valve be required
> > where the underground line feeds the existing house to prevent their
> > domestic demands from taxing the apartment system?
>
> > I've already designed it with two valves but am now second guessing
> myself.
>
> > Thanks,
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> > <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130117/b1ab2108/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>
> --
> Best regards,
>  Charles                            mailto:[email protected]
>
>  Confidentiality Notice: This e-mail message, including any attachments, is
>  for the sole purpose of the intended recipients and may contain
> confidential
>  and privileged information.  Any unauthorized review, use, disclosure or
>  distribution is prohibited.  If you are not the intended recipient,
> please contact
>  the sender by reply e-mail and destroy all copies of the original message.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130117/1e7da596/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to