Scot,

I think there are some interesting aspects to this question without too much
analysis of occupancy, type of operation, etc-- in other words, straight
from 13, but with a little extra thought. The job I mentioned in the earlier
post was an auditorium with a full compliment below the roof deck. There
were some ceiling clouds for acoustical reasons at various elevations and
various slopes. I think they were 16x16. (if they were 20x20, with any
slope, and we spaced based on slope, it would exceed 20). As you say, no
E.C. listed for greater than 2 in 12 Ceiling slope, BUT!:
I think that listing pertains to the single compliment of heads at the Main
Ceiling, which is the point of transition from mostly vertical to mostly
horizontal heat flow. A fire would have to be under the cloud for the head
in it to activate. In fact, the head would activate even if the cloud was
straight up and down, if the fire was directly below it, I think. 
It just strikes me that, at first thought, a 16x16 cloud at 2+ in 12 would
require 4 heads instead of 1. I appreciate your input.

ps-- ceiling clouds, being an obstruction, project a foot print on the
floor. if a 20x20 cloud sloped enough, that footprint would not exceed 48",
so not even 1 head required! :)

Brad  