Peerless has the TUF/TUTF horizontal split case multi-stage series - looks
like 750 gpm goes to 300 psi and beyond. No 1000 gpm UL/FM though. Single
stage AEF similar to Aurora, max 285 psi for the 1000 gpm

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, January 25, 2013 12:42 PM
To: [email protected]
Subject: 1000 gpm horizontal split case @ 300psi

I am too lazy today to actually go look for this myself, so I thought I'd
ask for some help.  Just off the phone with my A/C pump rep', who tells me
that the max. PSI rating they have on a 1,000 gpm horizontal
split case pump is 250 psi.   I know that Aurora goes up to 287 psi.
Any know of any that will hit 300 psi?   I'm trying to reduce the pump
rating to 750, which uncaps the pressure, but if the AHJ mandates 1000, we
may have to go in series.


Steve Leyton


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to