I think YES it applies. I also think that it would also be impractical to
protect these spaces...


On Mon, Jan 28, 2013 at 4:36 PM, Bobby Gillett <
[email protected]> wrote:

> OK - wood construction different job.
>
>
>
> We have one bidding that has 2x8 solid wood joists, they are attaching
> tongue-n-groove wood directly to the bottom of the joists.
>
> Does "NFPA 13 2010 - 8.15.1.2.5  Concealed spaces formed by ceilings
> attached directly to or within 6 in. (152 mm) of wood joist or similar
> solid
> member construction shall not require sprinkler protection." apply to this?
> It doesn't specify limited or noncombustible ceiling..
>
>
>
> Thank you,
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>  <http://www.keyfireprotection.com> www.keyfireprotection.com
>
>
>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130128/6e58fb86/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130129/c653b745/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to