8.15.1.2.6  would normally not require and additional fire stopping on our part 
for typical construction.  For a typical 12in TJI spaced 16in O.C. the required 
run would have to be over 120ft long before the 160ft^3 is exceeded.
  
 8.15.1.2.8 is only requiring the insulation in the space BETWEEN the bottom of 
joist and the ceiling, not the entire space.  Happens a lot with ACT ceiling 
installed 6in below the joists. 

Your right on about 8.15.1.2.7 and the non-3000ft^2 area, unfortunately the 
GC's are never wanting to do  this at their cost.

Dewayne

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, January 28, 2013 2:05 PM
To: [email protected]
Subject: Concealed Space - compsite wood joists

 

NFPA 13 - 2010:

8.15.1.2.6* <http://codesonline.nfpa.org/a/c.ref/ID00001327787/sec>
Concealed spaces formed by ceilings attached to composite wood joist 
construction either directly or onto metal channels not exceeding 1 in.
(25.4 mm) in depth, provided the joist channels are firestopped into volumes 
each not exceeding 160 ft3 (4.53 m3) using materials equivalent to the web 
construction and at least 3 1/2 in. (90 mm) of batt insulation is installed at 
the bottom of the joist channels when the ceiling is attached utilizing metal 
channels, shall not require sprinkler protection.

8.15.1.2.7   Concealed spaces entirely filled with noncombustible insulation
shall not require sprinkler protection.

8.15.1.2.8   Concealed spaces within wood joist construction and composite
wood joist construction having noncombustible insulation filling the space from 
the ceiling up to the bottom edge of the joist of the roof or floor deck, 
provided that in composite wood joist construction the joist channels are 
firestopped into volumes each not exceeding 160 ft3 (4.53 m3) to the full depth 
of the joist with material equivalent to the web construction, shall not 
require sprinkler protection.

 

I have a concealed space formed by composite wood joists with ceiling attached 
directly to the bottom of the joist (no metal channels, so insulation is not a 
requirement). If I'm not mistaken, in order to consider it a space that doesn't 
require sprinkler protection I have to do the
following:

Per 8.15.1.2.6 - Have the joist channels firestopped into volumes not exceeding 
160 ft³ OR

Per 8.15.1.2.7 - Completely fill the space with noncombustible insulation OR

Per 8.15.1.2.8 - Completely fill the space with noncombustible insulation AND 
have the joist channels firestopped into volumes not exceeding 160 ft³ (WHICH 
KICKS 8.15.1.2.7 OUT FOR COMPOSITE WOOD JOISTS ALTOGETHER)

 

I guess what I am misunderstanding is if I have to firestop the joist channels 
into volumes not exceeding 160ft³ either way, why would we want to fill the 
joist space completely with noncombustible insulation? Only thing I could think 
of would be to keep from having to do a 3000ft² RA in the adjacent protected 
space. 

 

Any comments for my understanding would be appreciated.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130128/9cef5418/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to