Kevin, 

Can be done, depends on the fire department in your area, usually written off 
as training. 

A couple of cautions: 

1. Keep pedestrians away, discharge hose will be at 250 psi

2. Vent all air from the system at the highest elevation outlet 

3. Ensure the pumper driver has the circulation relief valve open, as you will 
be discharging against a closed system (No flow) 

4. Use a good gauge at some out on the standpipe system, pumper gauges may not 
be accurate. 

If there is any UG piping don't expect it to pass, I've seen it fail many times 
at no more than 150 psi. 

Yours truly, 

Frank J. Herrick 
Kansas City, MO.  

-----Original Message-----
From: MOWLE Kevin(K) - BRUCE POWER [mailto:[email protected]] 
Sent: Friday, January 25, 2013 9:01 AM
To: '[email protected]'
Subject: Dry Standpipe 5 year pressure test enquiry.

 
As per NFPA 25(2011)  6.3.2  there is a 5 year requirement for the hydrostatic 
pressure test of dry standpipes. 

We are looking at the possibility of utilizing a Fire Truck (pumper) to 
complete this test. 

Has anyone else done this? Opinions?

Thanks
Kevin Mowle
Bruce Power
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to