Topic name shift....,

Also, if you are removing the head for an "inspection" inside the fitting,
you are performing tasks per 25, and must supply a new sprinkler.

R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeff Hewitt,
PE
Sent: Thursday, February 28, 2013 3:24 PM
To: [email protected]
Subject: RE: Bedbugs

Check NFPA 13, 2013, 6.2.1.1 


Jeff Hewitt, PE, SET  |  Corporate Engineer NICET #102015  |  Water Based
Layout - Level IV Inspection Testing & Maintenance - Level III

241 Hughes Lane  |  St. Charles, MO 63301 Office 636-946-0011  |  Fax
636-946-5172 Cell 314-574-6989  |  www.bistatefire.com

Fire sprinklers save lives.  Can you live without them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John O'Connor
Sent: Thursday, February 28, 2013 1:44 PM
To: [email protected]
Subject: RE: Bedbugs

Gentlemen:

Paragraph 6.2.1 (2007 Ed. NFPA-13) states:  "Only new sprinklers shall be
installed."
This refers to new work.  We relocate sprinklers in office environments all
the time.  Where does it say specifically that if you unscrew and remove a
head, you replace it?  What about general maintenance such as internal
inspections, where one head is to be removed for a visual inspection inside
the fitting?  You infer that the only correct action is replacing every head
you ever remove.  I say you are reading more into the code than intended.
If they wanted only new heads for every action, they (the committee) would
have said so. 

Reference also the 2002 edition of the Automatic Sprinkler Handbook, page
106, para 6.1.2.2 where they discuss reconditioned components.  "However,
when sprinklers have been installed in a building on a temporary basis--for
example, prior to finish ceiling work--the same sprinklers can be used on
that job.  The same holds true for an existing system that is being lowered
to accommodate a new ceiling provided the sprinklers are of the proper
orientation and the associated hazard has not changed."

The committee has clearly allowed relocated heads to be used.  If the
occupancy has not changed, the original head, as in the case of the bed-bug
remediation example, can be reused.  Obvious exceptions are if the head(s)
are 50 years or older, or of the wrong orifice, temp, thread size etc,
precluding its applicability as a suitable head for reinstallation.

John O'Connor 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Denhardt
Sent: Thursday, February 28, 2013 12:19 PM
To: [email protected]
Subject: RE: Bedbugs

Absolutely


John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd - Work
Sent: Thursday, February 28, 2013 1:18 PM
To: [email protected]
Subject: Re: Bedbugs

Aren't you supposed to replace with new heads if the old ones are unscrewed?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1430 / Virus Database: 2641/5638 - Release Date: 02/28/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to