Here is a strange issue I ran into this morning. Take a look at 8.15.7.3 and 
8.15.7.4, "Sprinklers shall be permitted to be omitted" and then take a look at 
8.15.8.1.1 and 8.15.8.2 "Sprinkler shall not be required" and "Sprinklers are 
not required".

I have an AHJ that says since 8.15.7.4 states "shall be permitted to be 
omitted" they stated we are not permitting them to be omitted. Has anyone seen 
this before or know why there is different terminology used between the 
sections. The way I see it is that sprinklers are either required by code or 
allowed to be omitted if the criteria is met.