Good morning all, Here is a strange issue I ran into this morning. Take a look at 8.15.7.3 and 8.15.7.4, "Sprinklers shall be permitted to be omitted" and then take a look at 8.15.8.1.1 and 8.15.8.2 "Sprinkler shall not be required" and "Sprinklers are not required".
I have an AHJ that says since 8.15.7.4 states "shall be permitted to be omitted" they stated we are not permitting them to be omitted. Has anyone seen this before or know why there is different terminology used between the sections. The way I see it is that sprinklers are either required by code or allowed to be omitted if the criteria is met. Eric Tysinger CET NICET III - 108988 Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, Inc. 4683 Laredo Ave. Fort Myers, Florida 33905 p: (239)433-3030 x1240 f: (239)433-3263 C: (239)633-9703 For Fire Alarm Service and Monitoring questions contact us at: [email protected]<mailto:[email protected]> "Ask us how we can eliminate your Fire Alarm phone line bills" "Ask us about CCTV, Access Control and Security" Thank you, and have a great day ! -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130307/986eda61/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum