I am dealing with this right now on a car dealership (service area). The
research conducted won an award in 2012. It is all still new and making its
way into the codes now. Bottom line, sprinklers will work and not be
obstructed, but the fan needs to be shut down within 90 seconds. Some have
this built in others may not. The only thing I could think of if not is a
shunt trip like we use in elevators.
Here is a video from a leading expert that helps...



http://www.youtube.com/watch?v=gEjjr_v2vis


R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
AKS-Gmail-IMAP
Sent: Thursday, March 14, 2013 12:19 AM
To: [email protected]
Subject: Re: HVLS Fans

No, but it makes sense to turn them off upon smoke detection so that they
allow the smoke to collect and stay up near the roof away from the public.
An air sampling smoke detection manufacturer claims their detector is built
into BA fans for this purpose, but that seems like a bad idea for
maintenance reasons. If it is a basketball gym then make sure the fans are
structuraly decoupled from the basketball goals. That might be very hard to
do. Gym roof are light. Otherwise you'll be getting a call from the owner
about the hoops vibrating with the fans.  

Allan Seidel
St. Louis, MO

On Mar 13, 2013, at 6:23 PM, Sharon Alves <[email protected]> wrote:

> Has anyone had any experience with the HVLS fans in facilities other 
> than storage?
> 
> 
> 
> Thank you,
> 
> 
> 
> SHARON ALVES
> 
> Senior Fire Sprinkler Designer
> 
> 
> 
> LP Consulting Engineers, Inc.
> 
> Mechanical - Electrical - Plumbing Engineers - Fire Protection
> 
> 1663 Eureka Road
> 
> Roseville, CA 95661
> 
> P: 916.771.0778 - F: 916.783.9446
> 
> <mailto:[email protected]> [email protected]
> 
> www.lpengineers.com
> 
> 
> 
> This email and its attachments are the sole property of LP Consulting 
> Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  
> This communication with its contents may contain confidential and/or 
> legally privileged information. It is solely for the use of the 
> intended recipient(s). Unauthorized interception, review, use or 
> disclosure is prohibited and may violate applicable laws including the 
> Electronic Communications Privacy Act. If you are not the intended 
> recipient, please contact the sender and destroy all copies of the 
> communication.  The sender and its company do not guarantee that this 
> email or its attachments is free of viruses nor does it accept any
liability for same.
> 
> 
> 
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20130313/11dbf91f/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to