See section 11.3 Residential in 2010 NFPA 13. Residential areas and adjacent corridors are allowed by NFPA 13 by calculating just 4 sprinklers with a .10 density or with residential flows whichever is greater....
Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Easter, Timothy Sent: Tuesday, March 19, 2013 12:04 PM To: [email protected] Subject: hydraulic design approaches I am reviewing a dormitory. The designer used the room design method (laundry, telephone room, and corridor), special consideration method - residential heads (bedrooms), and the density/area method (day room, computer lab). He is using NFPA 13, and not NFPA 13R. Basically he needs to increase the fire resistance rating of walls equal to water supply duration for room design method. Or he can re-design area to use density/area method. My question is if he chooses to use the density/area method, can he still use special consideration method - residential heads, which allows four heads inside bedrooms for calculation? Regards, Timothy Easter E.I.T. Graduate Fire Protection Engineer URS Corporation 11832 Rock Landing Drive Suite 306 Newport News, VA 23606 Direct: (757) 383-6217 [email protected]<mailto:[email protected]> This e-mail and any attachments contain URS Corporation confidential information that may be proprietary or privileged. If you receive this message in error or are not the intended recipient, you should not retain, distribute, disclose or use any of this information and you should destroy the e-mail and any attachments or copies. -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20130319/e393d28e/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2240 / Virus Database: 2641/5688 - Release Date: 03/19/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum