I'd second that recommendation.  Going electric with a generator makes no 
sense.  Go Diesel and be done with it.  I did a project in 2011 with 4000 gpm 
diesel driven VT's.  

Plus, nowhere in NFPA 20 does it state that a generator is permitted as the 
primary power source.  Every text you find related to a generator is stating 
use as an alternate or backup power source.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Tuesday, April 09, 2013 10:46 AM
To: [email protected]
Subject: RE: generator as primary supply

May I suggest that you consider a diesel driver with a right angle gear drive 
for the VT pump. This is an approved method and likely less costly.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Monday, April 08, 2013 9:13 PM
To: [email protected]
Subject: Re: generator as primary supply

Does it qualify as a power production facility John Drucker - Mobile Email

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected] <[email protected]>
Sent: Mon Apr 08 20:40:33 2013
Subject: generator as primary supply

I am looking at a job where the spec calls for an electric VT fire pump with a 
generator as primary electric supply. (Only single phase in street.) I know it 
can be done mechanically but I am not aware of any approved system.
Is there such an animal?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130408/37aeeda5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2240 / Virus Database: 2641/5734 - Release Date: 04/09/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to