I'd second that recommendation. Going electric with a generator makes no sense. Go Diesel and be done with it. I did a project in 2011 with 4000 gpm diesel driven VT's.
Plus, nowhere in NFPA 20 does it state that a generator is permitted as the primary power source. Every text you find related to a generator is stating use as an alternate or backup power source. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Art Tiroly Sent: Tuesday, April 09, 2013 10:46 AM To: [email protected] Subject: RE: generator as primary supply May I suggest that you consider a diesel driver with a right angle gear drive for the VT pump. This is an approved method and likely less costly. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Monday, April 08, 2013 9:13 PM To: [email protected] Subject: Re: generator as primary supply Does it qualify as a power production facility John Drucker - Mobile Email ----- Original Message ----- From: [email protected] <[email protected]> To: [email protected] <[email protected]> Sent: Mon Apr 08 20:40:33 2013 Subject: generator as primary supply I am looking at a job where the spec calls for an electric VT fire pump with a generator as primary electric supply. (Only single phase in street.) I know it can be done mechanically but I am not aware of any approved system. Is there such an animal? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20130408/37aeeda5/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2240 / Virus Database: 2641/5734 - Release Date: 04/09/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum