While true, aren't all the designs fixed to the grid with screws.  I seem to 
recall a cut sheet saying all was well without restraint but it's been years 
since I've seen one. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Law, Kevin 
W
Sent: Thursday, April 18, 2013 2:47 PM
To: Mike Hairfield; AFSA SprinklerFORUM
Subject: RE: NFPA 13-2007 Paragraph 9.2.3.4.4

The impulse from the jet from the fire sprinkler would still push the head up 
into the space, but the flexible connection would not transter that force back 
to the pipe.  Depending on the orientation of the connection of the flexhead 
pipe to the branch line would determine what resulting force would be resisted 
by the branchline piping.  That is, if the connection is facing down on the 
branchline piping, there is still a resulting upward force on the branchline 
pipe and visa versa if it is facing up. 

Therefore, the head would still need to be restrained or it would whip around 
like crazy upon discharge (have you seen the youtube videos of the red-neck 
riding a fire hose hanging from a crane......pretty wild stuff). 

Kevin Law, PE
Fire Protection Engineering
WTP Project - Bechtel National
Ph.   509-371-8296
Cell   509-531-0093
 

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Mike Hairfield
> Sent: Thursday, April 18, 2013 10:24 AM
> To: AFSA SprinklerFORUM
> Subject: NFPA 13-2007 Paragraph 9.2.3.4.4
> 
> Does anyone have data that says that flexible drops are an approved 
> for preventing the upward thrust thus preventing the sprinkler head 
> from lifting up into the concealed space.
>  
> Thanks,
>  
> Mike Hairfield
>  
>                                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-fir
esprinkler.org
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to