So, if it does not have a secondary power source it would not be a Dedicated
Function Fire Alarm Control Unit?

I don't believe the committee had a fire pump controller in mind when this
change was made. I never have thought of a fire pump controller as a
component of a fire alarm system, but I'm willing to be educated.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Failla,
Daniel
Sent: Tuesday, May 07, 2013 2:52 PM
To: '[email protected]'
Subject: RE: fire pump controller detection requirement

Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: [email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Easter,
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: [email protected]
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to