If 4 feet and over, there is no option, you need heads above and below. If less 
than 4 feet (as in your case), you may not need heads below if the heads above 
comply with the obstruction rules. Also depends on if the heads above are 
minimum 18" above the top of the obstruction or not.

Tony

----- Original Message -----
From: [email protected]
To: [email protected]
Sent: Thursday, May 9, 2013 8:50:19 AM
Subject: Ceiling Clouds vs Duct <4'

Have 3'-10" wide x 30' long clouds 8' on center in a large light hazard room. 
Anyone see a problem with saying they are less than 4' wide and don't require 
heads below?

Ron F