Funny. I thought it would be easy to find, but no, at least not in the 2011
edition. There's the 5-year hydro on dry sections (I think), and
obstruction investigation triggers, but apparently the backflush isn't a
scheduled maintenance thing.


On Wed, May 8, 2013 at 10:48 AM, Ford, Charles <[email protected]> wrote:

> I have understood that back flushing of the FDC was a routine thing. Some
> FDC checks have features the make it easier. Funny thing, I can't find it
> referenced in 25. Is this a local (Philadelphia) thing?
>
> C. Burton Ford
> NICET Certified IV
> NFPA Certified Fire Protection Specialist
> Cintas Fire Protection Inc
> 1038 Conshohocken Rd
> Conshohocken, PA 19428
> Tel 610-233-1400
> Fax 610-233-1401
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, May 08, 2013 12:49 PM
> To: [email protected]
> Subject: RE: Extending the design basis 15 ft. past...CALC?
>
> The intention is to provide a buffer zone between two dissimilar hazards
> where the higher density extends 15 ft beyond the physical end of the
> higher  hazard.  This way if a fire began at the edge of the higher hazard
> area, the higher discharge sprinkler system is more likely to respond than
> if you ended the sprinkler systems right at the imaginary line which
> physically separates two different areas of use.
>
> It has nothing to do with where you place the hydraulic design area.
>  That's dependent on your layout.
>
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> On May 8, 2013, at 9:14 AM, Ralphy Henderson <[email protected]>
> wrote:
>
> > Hello, NFPA 13 quoted at bottom w/ the relevant code section:
> >
> > With the 15 ft. extending into the lesser hazard is the intention to
> make this extended area part of the hydraulic design area (to be included
> in calcs) or simply to extend the results of the calculations into this
> area? My impression is the latter but I would like to see if people concur
> with that.
> >
> > Thanks,
> > RB
> >
> >
> >
> >
> >
> > NFPA 13: 2007
> >
> > 11.1.2
> >
> > (1)     Where areas are not physically separated by a barrier or
> partition capable of delaying heat from a fire in one area from fusing
> sprinklers in the adjacent area, the required sprinkler protection for the
> more demanding design basis shall extend 15 ft (4.6 m) beyond its perimeter.
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> This e-mail transmission contains information that is intended to be
> confidential and privileged. If you receive this e-mail and you are not a
> named addressee you are hereby notified that you are not authorized to
> read, print, retain, copy or disseminate this communication without the
> consent of the sender and that doing so is prohibited and may be unlawful.
> Please reply to the message immediately by informing the sender that the
> message was misdirected. After replying, please delete and otherwise erase
> it and any attachments from your computer system. Your assistance in
> correcting this error is appreciated.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to