What's the panel made of? You may have no panel in a fire.

On Wed, May 15, 2013 at 9:36 AM, Steve Leyton <[email protected]>wrote:

> So this lens creates a flat and continuous projection along the plane of
> the underside of the roof?   Agree that you don't need a sprinkler in
> the skylight ... unless you consider the space above the lens to be a
> combustible concealed space.
>
>
> Steve Leyton
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Mike Hairfield
> Sent: Wednesday, May 15, 2013 9:03 AM
> To: [email protected]
> Subject: Skylights
>
>
>  I have a project where the skylights are more than 32  sq.ft. in area
> which normally
>
> would require sprinkler protection, my project has a translucent panel
> attached at the roof
>
> line sealing off the skylight thus eliminating a ceiling pocket.
>
>
>
> My thoughts since there is not a ceiling pocket then sprinklers would
> not be required for this
>
> type of skylight.
>
>
>
> Any opinions?
>
>
>
> Mike Hairfield
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)