Except that you are designing outside the standard. 
Can't recall ever even thinking of approaching an AHJ with 6 psi instead of 7. 

Sent from my iPhone

On May 21, 2013, at 9:58 AM, "Brad Casterline" <bcasterl...@fsc-inc.com> wrote:

> Thanks John. Assuming that is true, we could say a 1/2" head at 7 psi throws
> 7'-6" each way. At 7 psi the water hits the deflector going 32.26 ft/sec.
> v=SQRT(2gh). At 6 psi it would be going 29.87 ft/sec, and would throw 6'-11"
> each way.
> 
> -----Original Message-----
> From: John O'Connor [mailto:jocon...@nfspk.com] 
> Sent: Tuesday, May 21, 2013 8:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: calc procedure logic
> 
> The 7.0 PSI end head minimum pressure was never intended to "kick out" the
> links, seat etc, but to develop the minimum spray pattern required to
> deliver the specified density.
> John O'Connor
> National Fire Sprinklers, Inc.
> Nashville TN
> 
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> mphe...@aerofire.com
> Sent: Tuesday, May 21, 2013 8:31 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: calc procedure logic
> 
> Wouldn't it depend on the application rate, area of protection and orifice
> size?
> Mark at Aero
> 
> ----- Original Message -----
> From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
> Sent: Tuesday, May 21, 2013 01:03 PM
> To: sprinklerforum@lists.firesprinkler.org
> <sprinklerforum@lists.firesprinkler.org>
> Subject: calc procedure logic
> 
> Would the 7 psi minimum operating pressure from NFPA 13 Calculation
> Procedure apply to open head deluge, since the operating parts have already
> been ejected clear of the frame and deflector by a ball-peen hammer?
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> bcasterl...@fsc-inc.com
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1432 / Virus Database: 3162/5841 - Release Date: 05/20/13
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to