If these are modular homes its likely cpvc that isn't going anywhere. 

Sent from my iPhone

On May 25, 2013, at 11:46 PM, "Ron Greenman" <rongreen...@gmail.com> wrote:

> Whether or not the system would sway during moving would be dependent on
> how it's currently installed. If in earthquake country it wouldn't sway
> since it would be braced against seismic events. Pre-fabs are designed to
> be moved so swaying is minimized by sway bracing or hung in such a way as
> to compensate.
> 
> 
> On Sat, May 25, 2013 at 8:35 PM, David Canham <dcan...@firesys.com> wrote:
> 
>> They put the sprinklers in off site for manufactured buildings all the
>> time, is this that different? All the other trades get installed before
>> shipping as well.   I was doing some work for a company a whole back that
>> built all the building in there factory and they had sprinklers installed
>> during fabrication then shipped the units to the site for final assembly.
>> They connected piping from one module to the next in the field. It seemed
>> to work fine. All calculations were done based on the local supply.
>> Plumbing and gas was done the same way. Drop it on the foundation and
>> connect the utilities.
>> 
>> David Canham
>> Fire Systems Solutions
>> 
>> Sent from my iPhone
>> 
>> On May 25, 2013, at 4:57 PM, Todd - Work <t...@fpdc.com> wrote:
>> 
>>> In addition to those, my concern would be that if the pipe is suspended
>> from the structure, it will probably sway back and forth during the move
>> and could possibly damage heads or pipe.
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 
>>> On May 25, 2013, at 12:54 PM, "Douglas Hicks" <fire...@eoni.com> wrote:
>>> 
>>>>  An account is moving a pre-fab building.  The occupancy is classrooms
>> and office space.  They want us to disconnect and connect the sprinkler
>> piping in the attic.  But, as I am considering this, I keep coming up with
>> more concerns.  Some of which, in not particular order,  are:
>>>> 1. They will need to have a FPE run the supply calcs for the new
>> location.
>>>> 2. The standard will be NFPA 13-2013, which will require a pit, an FDC,
>> backflow devices, and a way to perform a Full Flow Test.  I think I should
>> have someone experienced in underground do all that.
>>>> 3. The present water supply comes into the building from the floor.
>> Should we disconnect and remove the riser to protect it from damage during
>> transport?
>>>> 4. The area has a history of water deposits in piping.  When we lived
>> in that town, I would reverse flush the potable water lines using air.  I
>> was  amazed at the debris that came out of the water piping. As a result, I
>> never had the low water pressure my neighbors had, nor did I need to
>> replace the piping.   I think the sprinkler piping should be flushed prior
>> to shutting off the water and draining the piping.
>>>> 5. After the building is in place, the piping will need to be
>> assembled.  I do not know if the attic piping is steel or plastic, I expect
>> plastic.  Whatever the material, I think a hydro-test is a good idea.
>>>> 
>>>> Any other suggestions?
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> rgreen...@bates.ctc.edu
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to