I am working on an existing building where there is an unheated enclosed porch 
approximately 8 ft deep and 18 ft wide. The space is occupied by a few plant 
and two 2' high plan drawers. My original plan called for 2 dry sidewalls. 
Unfortunately there is a steel beam and the highest that a sidewall could be 
mounted is 15" below the ceiling. Are there and dry sidewall listed for below 
12"? I couldn't find anything but thought the greater group might know. Heating 
the space or installing a heated soffit is DOA. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com